*ALERT*ALERT*ALERT*ALERT*
FIRE ALARM INSPECTION / TEST
PLEASE POST CENTRALLY IN YOUR DEPARTMENT
FACILITIES MANAGEMENT WILL BE INSPECTING / TESTING THE FIRE ALARM SYSTEM IN BLDG:
1602 UVA Orthopedic Center Ivy Road
Fire Alarm Chimes and Strobes Will Be Activated From: 05:00 06:00
***Please Review Your Local Downtime Activation Plan in Advance of This Test***
While no interruptions in service are expected, beyond those indicated in this notice, you should review your local area response plan prior to the test. For unexpected issues related to this test please report to Help Desk at 4-2267 and your local clinical leadership for operational response.
Additional Information:
Fire Doors Will Close
|
|
AHUs Will Shut Down & Immediately Restart
|
|
AFFECTED AHUs:
|
AHU 3-1 SUPPLY AHU3-2 RETURN AHU-3 RETURN AHU 3-2 SUPPLY AHU 3-2 &3-2 RETURN AHU 3-3 RETURN AIR AHU 3-3 SUPPLY GROUND FLOOR MECH ROOM GROUND FLOOR MECH ROOM
|
|
|
Details Of Testing:
Scheduled Dates: |
February 24, 2025 at 5:00:00 AM EST - February 26, 2025 at 2:00:00 PM EST
This Outage Will Occur Daily: 05:00 14:00 |
Work Order Number: |
3952998
|
POC For Testing: |
Matthew Brown 434-566-7878
|
Approved By: |
Richard Good (UVA FM HSPP) |
Additional Notes for Fire System Maintenance Personnel
Note 1: Ensure there is not any troubles on the fire panel when system is back in service
Note 2: Per State Fire Marshal - Fire watch must be provided when the fire alarm or sprinkler systems are out of service. HSPP Fire Marshal must be notified 24 hours prior to taking the system offline by email:
Note 3: Submit fire watch log and documentation to Jeff Smith, Sr. Compliance Manager at conclusion of testing
Note 4: Contact HSPP Service Desk (4-8091) and Systems Control (2-4685) prior to starting and upon completion of all work
*ALERT*ALERT*ALERT*ALERT*
Please use the below link to unsubscribe from these notification, change, or subscribe to other building lists